Toggle Sw. off but sw leg still hot

Status
Not open for further replies.

EEC

Senior Member
Location
Maryland
I went to change out two ceiling mtd' fixtures for HO. Turned off toggle sw to work on the ceiling fixture outlet, only to find that the sw leg was still hot. This occured at both locations. It seems that the switches are switching the neutral. The fixtures worked fine before and after installation of new fixtures wired no different then before. Any comments would be welcome.
 

Pullnwire

Senior Member
Location
Surrounded by Oranges
Occupation
Electrician, Business Owner, SME and Trade Instructor
Were the switches lit? A tic tracer will show voltage, as power is feeding through the switch to the lamp so it will glow.
 

EEC

Senior Member
Location
Maryland
Clarification

Clarification

Were the switches lit? A tic tracer will show voltage, as power is feeding through the switch to the lamp so it will glow.

No matter whether the switch was off or on, there was a hot wire still at the fixture outlet.
 

PCN

Senior Member
Location
New England
I'd either open up the switch to see if the neutrals are connected to the terminals on the switch.
Or take down the fixture put one lead of your meter on the hot, put the other lead on the grounding conductor, flip your switch on and off. If it stays energized in either position that will tell you the hot is not being switched. Repeat with the hot and white to confirm.
 

electricmanscott

Senior Member
Location
Boston, MA
I went to change out two ceiling mtd' fixtures for HO. Turned off toggle sw to work on the ceiling fixture outlet, only to find that the sw leg was still hot. This occured at both locations. It seems that the switches are switching the neutral. The fixtures worked fine before and after installation of new fixtures wired no different then before. Any comments would be welcome.

How old was the house?

Very common in old houses.
 

220/221

Senior Member
Location
AZ
I wouldn't have, couldn't have left without figuring it out and correcting it.

Kind of hard to troubleshoot via the internets :roll:
 

Ed Carr

Senior Member
Location
way upstate NY
EEC, If you have two switch locations and a wire at the fixture that's
always hot it's probably a bootleg 3way.The neutral is switched at one
end and the hot at the other.480 Sparky had a nice little display of it.

Ed
 

480sparky

Senior Member
Location
Iowegia
EEC, If you have two switch locations and a wire at the fixture that's
always hot it's probably a bootleg 3way.The neutral is switched at one
end and the hot at the other.480 Sparky had a nice little display of it.

Ed

Both the hot and neutral are switched at both 3-ways.

Calif3wayanim.gif
 