I have been asked to do something I do not know how to do.
Sizing a TOL for a motor is no big deal, but I have been asked to deterine if the TOL has enough margin after it has been in use to restart the motor after a stop.
Here's the scenario: Motor is running, plant receives accident signal, load sheeding that includes the motor under consideration, motor reloaded to system after 300 seconds.
The question is, will the TOL isolate the motor when it is required to restart, and what, if any, is the margin available assuming it does not isolate.
I understand the idea here: TOL heats up as the motor is running to some value. Load is shed and TOL begins to cool. 300 seconds pass and load is required to restart. The inrush current over the period of starting will heat the TOL. Will the restart cause a trip? If it will NOT cause a trip, what is the margin available?
I just have no idea where to find this sort of information. Has anyone ever come across this before? Does anyone have any suggestions on where to start?
I know you will ask, so here is the existing motor data: 3-phase, 460V, 3HP, FLI=3.9A, LRI=31A, SF=1.15, starting time=6 sec., TOL=Siemens K33
I know the starting time is long, but it's what I was told to assume. This motor is for a 6.9kV shutdown board room chiller package oil pump.
Sizing a TOL for a motor is no big deal, but I have been asked to deterine if the TOL has enough margin after it has been in use to restart the motor after a stop.
Here's the scenario: Motor is running, plant receives accident signal, load sheeding that includes the motor under consideration, motor reloaded to system after 300 seconds.
The question is, will the TOL isolate the motor when it is required to restart, and what, if any, is the margin available assuming it does not isolate.
I understand the idea here: TOL heats up as the motor is running to some value. Load is shed and TOL begins to cool. 300 seconds pass and load is required to restart. The inrush current over the period of starting will heat the TOL. Will the restart cause a trip? If it will NOT cause a trip, what is the margin available?
I just have no idea where to find this sort of information. Has anyone ever come across this before? Does anyone have any suggestions on where to start?
I know you will ask, so here is the existing motor data: 3-phase, 460V, 3HP, FLI=3.9A, LRI=31A, SF=1.15, starting time=6 sec., TOL=Siemens K33
I know the starting time is long, but it's what I was told to assume. This motor is for a 6.9kV shutdown board room chiller package oil pump.