Too far to trip relay??
Honeycone
Phoenix
Gentlemen...I just registered and my last question was answered so wonderfully I am beginning to have more trust in this forum than my coworkers.
Here's the question: I have an air compressor that has a control panel as part of it. The compressor control panel has pins to turn it on, tell you if its running etc, there is also a 24vdc to "wet" the contacts. I want to interface this air compressor with a VFD about 6-700 feet away. I have a pump that I want to turn on at the same time as the Air compressor, and I show a control panel near my pump ( and 600') from my air compressor. This control panel via a relay contact closes the pins to the air compressor and pump at the same time via a 120v relay.
Does the 120v relay simply close each contact for the pump and air compressor and will I have to apply a 24VDC source to the compressor and the pump ( the pump run signal is given via a VFD, so really im closing the VFD run contacts)
I think I can close the air compressor contacts fine with a relay and then apply a 24vdc to the air compressor start pin, but what about a signal back from the compressor that says its running?
I am good enough to be dangerous with this stuff hahaha, thank you!
Here is a picture showing the start/stop pin and a 24vdc next to it....so just connect the two and place my relay contacts n between them for control??
Confusing
you need to start 2 machines
a compressor w/starter cntl pnl
a pump w/vfd
what starts the compressor?
low pressure?
manuall?
the pump
sounds like you want it interlocked with the comp
when the comp starts the pump starts
need the control pnl and vfd dwgs
"....has pins to tell you it is running...."
Can you be more specific? Likely you can use the signal to start the pump, but in order to be more helpful, we need more info.
My best guess is that means there is terminals connected to an aux contact that changes state when the drive is "running", or possibly even a digital or analog output that changes state when "running". The limitiation is that it tells you there is an active run output, but may not tell you if the compressor is actually "compressing". Motor to compressor coupling issues, or mechanical failure within compressor could leave you with motor running but no pressure being developed - if you want to detect that situatiuon, a pressure switch is maybe the way to prove what you want before starting the other pump.