Ravenvalor
Senior Member
- Location
- Piedmont region of NC
Hello,
I looked at a dimmer pack in a large (1,000-seat) church that had a 1.25" PVC raceway with a whopping 32 - current carrying conductors in it (16-ungrounded and 16-grounded. About 8 of them were terminated on 20-amp rated circuit breakers and the other 8 were not terminated at all but were intended to be terminated onto 20-amp circuit breakers at a later date. To me the code violations are two-fold. The first is the PVC in a place of assembly and the second is the overfill of the raceway. This installation was made in the early nineties. I was wondering if the installation met the NEC requirements of the early nineties? I would like to utilize those other unused conductors onto 20-amp circuit breakers.
Thank You,
I looked at a dimmer pack in a large (1,000-seat) church that had a 1.25" PVC raceway with a whopping 32 - current carrying conductors in it (16-ungrounded and 16-grounded. About 8 of them were terminated on 20-amp rated circuit breakers and the other 8 were not terminated at all but were intended to be terminated onto 20-amp circuit breakers at a later date. To me the code violations are two-fold. The first is the PVC in a place of assembly and the second is the overfill of the raceway. This installation was made in the early nineties. I was wondering if the installation met the NEC requirements of the early nineties? I would like to utilize those other unused conductors onto 20-amp circuit breakers.
Thank You,