A friend had a job fail inspection. The building was put together with modular units, the units came with 200 amp main breaker panels. My friend mounted 200 amp mbp's with 8 spaces and feedthru lugs (trailer panels) on the exterior. These were fed from a 1600 amp service, 200 amp breakers in a distribution panel.
The inspector (North Carolina) said there was a limit of 2 main breakers, and my friend took the 200 amp main breakers out of the factory installed mbp's and put in main lug kits to pass inspection.
Where is this in the NEC?
The inspector (North Carolina) said there was a limit of 2 main breakers, and my friend took the 200 amp main breakers out of the factory installed mbp's and put in main lug kits to pass inspection.
Where is this in the NEC?