50% says YES, AWG 4 THHN can be use as a feeder for a 100 amps sub-panel and 50% says NO for a separated garage/shop. I am in doubt, but I would like to use it as I have a full spool and I am donating it.
Use it with a 90A breaker and you will be just fine. Unless there is a serious growing operation going on in the garage the main will never trip.50% says YES, AWG 4 THHN can be use as a feeder for a 100 amps sub-panel and 50% says NO for a separated garage/shop. I am in doubt, but I would like to use it as I have a full spool and I am donating it.
Use it with a 90A breaker and you will be just fine.
You can still use the 100A panel with the #4 and I'll bet a hundred dollars you will be fine with a 60A breaker.Thanks! I don't know why I still listening to all those "opinionated individuals" outside the forum. Maybe it is my fault as I was trying hard to use a 100 amps panel and a spool of #4 that I have in stock because a 90 amps breakers are too expensive. Mea Culpa!
Maybe do a load calculation and see if I can install in the same box and in the main panel a 60 amps breakers and run this existing #4. Uggg
Happy Easter! ... Too late?
You only need the 90 at the supply end of the feeder. The one at the garage panel can be any size.I paid $40.00 for this load center including the 100 breaker and I have in stock an extra 100 for the main panel. If I have to buy two 90s it will be too expensive, but I have extra 60s, so I will do the load and see if 60 will be enough.
You only need the 90 at the supply end of the feeder. The one at the garage panel can be any size.
... Should the 100 be in the main and the 90 in the garage
If I can go with 60 (after load calculation) I can install a 60 breaker with the same #4 and the 100 sub-panel and it will be ready for future expansion. Thanks
Sorry, it makes sense. If I can go with 60 (after load calculation) I can install a 60 breaker with the same #4 and the 100 sub-panel and it will be ready for future expansion. Thanks
50% says YES, AWG 4 THHN can be use as a feeder for a 100 amps sub-panel and 50% says NO for a separated garage/shop. I am in doubt, but I would like to use it as I have a full spool and I am donating it.