Cjmeziere12
Member
- Location
- Oklahoma City
- Occupation
- Low Voltage Distribution Engineer
Hello, all.
Got a question regarding requirements for conductor entry into dry-type transformers.
Here's the situation: We have a 400Hz/600kVA step-up transformer (200Y-575Y) being installed. The installation team wanted to top-feed the transformer to cut down on install time (long story but it checks out) and I reasoned that it would be okay due to the transformer being largely oversized for the existing load and that, given an increase in load, we would go back and side-feed the transformer when we replaced the upstream conductors.
So, when my Senior Engineer found out, he informed me that he believed it to be against code to top-feed. I have done some research and haven't found it in the NEC yet, and it appears that it may be an installation requirement by the manufacturers in most cases (though there is no "wire below this line" tag on this transformer).
Is there somewhere in the code (NEC or otherwise) that lays out this restriction? Is it just a manufacturer requirement? I'm seeing a lot of discussion mentioning the prohibition of top-feed on dry transformers up to a certain kVA, would this somehow not apply to a 600kVA?
Any help appreciated,
Thank you!
Got a question regarding requirements for conductor entry into dry-type transformers.
Here's the situation: We have a 400Hz/600kVA step-up transformer (200Y-575Y) being installed. The installation team wanted to top-feed the transformer to cut down on install time (long story but it checks out) and I reasoned that it would be okay due to the transformer being largely oversized for the existing load and that, given an increase in load, we would go back and side-feed the transformer when we replaced the upstream conductors.
So, when my Senior Engineer found out, he informed me that he believed it to be against code to top-feed. I have done some research and haven't found it in the NEC yet, and it appears that it may be an installation requirement by the manufacturers in most cases (though there is no "wire below this line" tag on this transformer).
Is there somewhere in the code (NEC or otherwise) that lays out this restriction? Is it just a manufacturer requirement? I'm seeing a lot of discussion mentioning the prohibition of top-feed on dry transformers up to a certain kVA, would this somehow not apply to a 600kVA?
Any help appreciated,
Thank you!