300amps service 350ckmil undergraund iwant to top two ets of number 1-0 and feed to 150 mps main esconets to feed one transfer switch each and use the originals panels a subs do you gus see somethin wrong with this?
 
Re: tops on feeders {service}

Wilsa read the warning labels on the bottle "may impair you ability to drive or do not operate heavy machinery" :D :D

;) Every body be afraid be very afraid. :eek: :eek: :eek:
 
Re: tops on feeders {service}

do I see somthing wrong with this??? What's "this"?
Post again in english. (please)

[ January 05, 2006, 08:01 AM: Message edited by: shelco ]
 
Re: tops on feeders {service}

Hey, it must be the sinus drugs I'm on, becuase it makes sense to me.

I translate it as:
[I have a] 300A service [fed by] 350kcmil underground conductors. I want to tap these conductors with two sets of 1/0 and feed to two 150 amp main disconnects. [Each] disconnect will feed a transfer switch and [I will] use the existing panels as sub[panels]. Do you guys see anything wrong with this.
 
Re: tops on feeders {service}

Jim your good. :cool:

If what you translated is correct I would say it could be done code compliantly.

But that is a big jump of faith as we know so little.

Load calcs would need to be done to ensure the service conductors are sufficient.

The taps would need to be made properly, no 'double lugging'

The bonding of this new service disconnects would need to be done.

The 'taps' would be service conductors and would need to be short and protected from damage.

Just a lot we do not know.
 