ceb58
Senior Member
- Location
- Raeford, NC
I need some suggestions about a situation I have with some tower lights. One of our sites is a joint venture with a local electrical cooperative. We supplied a new building with generator and UPS and gave them space in the building for their equipment in turn we use their tower and they maintain the tower lights. Now the problem is the tower lighting system is an old 120v system with only marker lights and 2 strobes. The height of the tower only requires the lights to be on at dark and are controlled by a photo cell. The problem I am having is when the lights strobe I can watch the voltage on the UPS display go from 121v down to 116v per phase. The 116v is when the strobes are fully illuminated and the voltage will rise as the intensity decreases it repeats this 30 times per min. This is causing the UPS to switch back and forth from utility to batteries because the UPS only has a +/- 2v range. It also drives the 40kw generator crazy trying to keep up with the fluctuation. I have tried wiring the light controller in on a UPS circuit to see if the UPS would "filter" the voltage but it made no difference. The controller has no capacitor's just a relay for the solid markers and a flasher for the strobes. The markers are 150w incandescent and the strobes are 300w on a 300 ft. tower. My thoughts would be to install a buck/boost transformer between the panel and controller but not sure if this would decrease or eliminate the fluctuation ???