I have been hearing problems of new TP-1 xfmrs (low voltage distribution type 15-225kva 480/208Y-120v) having inrush currents up to 30X the primary full load and breakers tripping out on the xfmr, inrush, one manufacturers information listed a 35.6X multiplier and another listed 6.41 for the same size TP-1 xfmr. All other characteristics were pretty close (x%, r%, z%, losses etc.) just curious if there is a formula to calculate the inrush in amps or estimate it, I cannot figure out why the significant difference anyone else come across such an issue or have seen such large variations of the multiplier? Thanks.