There is a context for 210.52 that, in my opinion, can't be ignored. In addition to Chapter, Article and Section, there is "Part". The term "Part" comes from the NEC Style Manual and is explained there.
The NEC Style Manual says:
210.52 is in Part III of Chapter 2, that is:
I think this is where the words from 406.11, that is, "areas specified" is taken to mean "required outlets". I am understanding that "areas" as stated in 406.11 is not a stand alone term, but rather "areas specified" is a two word term.
The areas specified in 210.52 are the areas where outlets are required, and to be counted as the required outlet, the outlet has to be below 5?', not in a lamp or appliance, not in a cabinet or cupboard and not a lighting outlet (210.70(A)(1) Ex No. 1).
210.52 is not a simple list of areas.
To be a "specified area" in 210.52, IMO, a required outlet has to be present.
The area beside the required outlet, the area that can't have a required outlet, is not a specified area.
There is a context for 210.52 that, in my opinion, can't be ignored. In addition to Chapter, Article and Section, there is "Part". The term "Part" comes from the NEC Style Manual and is explained there.
The NEC Style Manual says:
2.1.4 Parts. If an article is sufficiently large, it shall be permitted to be subdivided into parts that correspond to logical groupings of information.
210.52 is in Part III of Chapter 2, that is:
The "logical grouping" that 210.52 is under is Required Outlets.2008 NEC
Chapter 2 Wiring and Protection
Article 210 Branch Circuits
Part III. Required Outlets
I think this is where the words from 406.11, that is, "areas specified" is taken to mean "required outlets". I am understanding that "areas" as stated in 406.11 is not a stand alone term, but rather "areas specified" is a two word term.
The areas specified in 210.52 are the areas where outlets are required, and to be counted as the required outlet, the outlet has to be below 5?', not in a lamp or appliance, not in a cabinet or cupboard and not a lighting outlet (210.70(A)(1) Ex No. 1).
210.52 is not a simple list of areas.
To be a "specified area" in 210.52, IMO, a required outlet has to be present.
The area beside the required outlet, the area that can't have a required outlet, is not a specified area.