peter d
Senior Member
- Location
- New England
We are currently finishing up a house that was wired under the '05 code. I'm installing all kinds of non-TR receptacles. I feel like such a rebel (even though it's pefectly legit.) 
I see it just as Scott does, all areas 'mentioned' by 210.52, not all receptacles required by 210.52.
It says what it says in plain English and does not say what it does not say.![]()
We are currently finishing up a house that was wired under the '05 code. I'm installing all kinds of non-TR receptacles. I feel like such a rebel (even though it's pefectly legit.)![]()
We are currently finishing up a house that was wired under the '05 code. I'm installing all kinds of non-TR receptacles. I feel like such a rebel (even though it's pefectly legit.)![]()
I always knew you hated children.:grin:
If it is a 15 or 20 amp 125 volt receptacle in any area addressed by 210.52 then it must be TR. There are no exceptions for height or any other reasons.
not even the outlet in the garage ceiling for the opener?
TR?? Is that the new receps that have the safety barriers built in
Not exactly but close-- crawl space does not require TR as far as I can tell nor does the attic recep. if you put one there.Plain and simple - if it is in a house use TR receptacles for all 15amp or 20amp 120v circuits,
Arc fault is not required in attics and I would venture to say not in laundry rooms , unless one can define a similar area. :smile:use arc faults for all 120v 15amp or 20amp non gfci protected circuits (except bathroom and kitchen).
Use a GFCI on the garage door openers, use a WR, TR GFCI receptacle with a bubble cover for outside receptacles, that is it. Well that isn't all of it but those are the rules for 2008.
use a WR, TR GFCI receptacle with a bubble cover for outside receptacles.
This means that ALL 15 or 20 amp 125 volt receptacles in:
Kitchens, Pantries, Breakfast rooms, Dining rooms and similar areas, Living rooms, Parlors, Libraries, Dens, Sunrooms, Bedrooms, Recreation rooms, & similar areas, Bathrooms, Outdoors, Balconies, Decks, Porches, Laundry Areas, Basements, Garages (attached or detached) , Hallways (...I think that is all of them ...)
mweaver
TR's are ridiculous.....whatever happened to evolution, survival of the fittest? However I don't care enough to go on a rant......