Track Lighting Current Limiting Feeds

Status
Not open for further replies.

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
In article 220, the load calc for track lighting is done based on the total feet installed, but there is no limit to the installed luminares on the track.

Heres a new product that limits the installed load to a specified amperage:
http://www.noralighting.com
I can't get the link to point to the page
do a search for current limiting power feeds,,,,sorry
 
Last edited:
as I recall I used to do a lot of large department store work and at one time I read the instructions with the track lighting I was installing and it said it was for a max of 1200 watts yet the stores would load up 20 ' or more with a million heads and the track would burn up and we would go out and replace it over and over and over. But I do remember that there was a max wattage for the track in the instructions at the time I was installing it.
 
Is this it?

nt358.jpg


NT-358
[FONT=Arial, Helvetica, sans-serif]In-Line Feed (One Circuit Track System)[/FONT]

[FONT=Arial, Helvetica, sans-serif]DESCRIPTION:
Nora Lighting's new "Current Limiter" provides the
solution you've been looking for to comply with
California Energy Code Title 24 and the continuing
Energy Efficient Standards set by other States. Nora's
"Current Limiter" is a UL Listed line voltage Track
power feed with an integral circuit breaker that limits the
current load on the track to a specified amperage/
wattage.

Breaker ampages: 1A, 2.5A, 5A, 7.5A, 10A, 12A, 14A

Finish: Black, White, or Silver

Listing: UL Listed
[/FONT]
 