TRAFFIC SIGNAL PHYSICALLY BONDED?
Trafficops
New User
Long Beach
Assistant traffic signal technician
How are traffic signal equipment bonded physically? Not grounded. Bonding of all metallic equipment.
Where exactly does it start? What is it bonding too? Does it start at the Edison service cabinet then the 332 cabinet to the poles and signal head?
I’m so confused because everything I read mentions grounding.
As Zbang states, most grounding is actually bonding. The title of Art 250 is Grounding and Bonding.
Not sure what a 332 cabinet is. I used to write articles for the International Municipal Signal Association and instructed classes for them. One class in Denver at the National Conference, I had an electrician from New York City (some 10,000 signals). based on what he learned in the class, New York made a change in how they grounded and bonded their signals.
At the service (Edison) the neutral is connected to the grounding electrode system by the Main Bonding Jumper. The EGC (grounds) all tie to this point which is to provide a path back the transformer, to clear a line to pole (case fault) and the fault current does not go to ground.
From your signal cabinet, there will be a EGC complying with 250.118 (please review this section) to the heads, poles and displays. The signals I worked on were almost all mast arms, so the poles were bonded to the EGC, and the heads, were screwed or clamped onto the arms.
What's different about traffic signals (pretty sure this is the same nation wide) is none of the equipment past the service is listed. Its just the way the signal industry does it, and every state and jurisdiction have there own standards, some reference the NEC, some don't. Our AHJs inspect the service and the agency has a label in the cabinet that states the agency acts as the certifying authority....This keeps the AHJs happy
So just make sure you have the ground fault return path per 250.118. If there are ground rods at the signal poles, thats ok, as long as they are not the return path for a fault, the ground rods are to be bonded to the EGC.
And as ZBang mentioned, lots of good videos from Mike Holt on grounding and bonding.
902.15.6.3 Ground Wire
Standard. A #6 AWG solid or stranded equipment grounding conductor, in conduit, shall be used to connect overhead mounted signal heads on bridge structures to the controller ground. A controller mounted on a structure is grounded by means of a #1 AWG, solid or stranded grounding electrode conductor in conduit connected to a ground rod in the first pull box located off the structure, providing the conductor length does not exceed 200 feet. Over this distance, a larger size wire is used as determined by calculation. Number 6 AWG, solid or stranded equipment grounding conductor shall be used to electrically bond all steel conduits in pull boxes to the power company ground. A properly sized equipment grounding conductor shall be provided in all conduits to provide an effective ground path from each post to the ground bus in the controller cabinet. Plan quantities are not computed for ground wire, but conduit is to be sized accordingly (see Table 902.15.6.1).