Traffic Signals, NEC or NESC?
kwired
Electron manager
NE Nebraska
When I Googled that type of cable, the one I saw only had 4 conductors. Red, Yellow, Green and Black.
I would have no trouble with the use of such color scheme for that particular application. But I guess some are afraid some handyman may service it some day and it would really confuse him:roll:
Having the right color of signal light on at the right times seems to be a life safety issue to me, and maybe you should be qualified to work on the thing as well.
RichB
Tacoma, Wa
Electrician/Electrical Inspector
We use either IMSA-5 or -7 conductor cable--depending on the number and configuration of the heads and intersection
IMSA-5--Black, white, red, green and orange
IMSA-7 adds blue and brown
K8MHZ
Is there such a thing as IMSA-5 or IMSA-7? All the IMSA cables I can find specs for start with 19 or higher.
I did find this color code, which says #7 should be white with a black stripe.
Table 5.1
Straight Conductor Color Code
Cables having more than 21 conductors are identifiable by
their location in the concentric layers in the cable assembly.
Conductor
Number Insulation Color Stripe Color
1 Black -2 White -3 Red -4 Green -5 Orange -6 Blue -7 White Black 8 Red Black 9 Green Black 10 Orange Black11 Blue Black12 Black White13 Red White14 Green White15 Blue White16 Black Red17 White Red18 Orange Red19 Blue Red20 Red Green21 Orange Green
https://www.ptsupply.com/solutions-library/Product Info/imsa-manual.pdf
brantmacga
Señor Member
Georgia
Former Child
In my area, signal installations are not permitted jobs. If it were private, probably, but there are none here I'm aware of.
If it's a state highway, the DOT has the utility install (GA Power), but usually it's done by their sub-contractor.
City streets are installed and maintained by the city.
DOT signals are not metered.
Anything the utility does here is not permitted or metered (site lighting, etc...); not sure if they use the NEC for that or NESC.
RichB
Tacoma, Wa
Table 5.1
Conductor
ok-- Sorry about that--We just call it IMSA-5
On the reel label it is listed as--14-5C IMSA 20-1 STR BC
And yes--the seventh wire is Wh/Bk--I was going from memory and for some reason thought there was a brown before it went striped