What is the proper way to ground and bond 2-generators with a 3-pole transfer switch ?
The generator is not bonded.
)What do you think about not bonding either generator and installing a bonding jumper at the first MDP. There would be no parallel paths as the gen sets would not be bonded. Any fault in either generator or transfer switch would get back to source.. comments ?
Well if you have a solid neutral in your transfer switch you can bond in the mdp
I just had an inspector tell me its ok in this scenario to bond only 1 gen set. Not sure i agree. I understand not bonding the generator when the other feed to transfer switch is prime power as the neutrals are connected. But 2 gen sets ? Comments ?
Ok, Bond both gen sets as seperately derived systems. Run 3-wire (phase conductors) to 3-pole transfer switch. No Equipment Grounding conductor to Transfer Switch.
Correctslect;980878) said:Install 3-wire to Transformer with an EGC. Bond as a seperately derived system.
Install 4 wire with an EGC from transformer to MDP. No System Bond at MDP.
Ok, Bond both gen sets as seperately derived systems. Run 3-wire (phase conductors) to 3-pole transfer switch.
I have read thru this thing, and for the life a me I can not figure out what the issue with bonding both generators and running four wires thru xfer switch to MDP. Floating the grounded conductor after generators, like what was first suggested. What am I missing?