Phil Forget about the neutral, just put it out of your mind. 
Now to make sure we are talking about the same thing.
We are talking about an existing MWBC in an existing panel.
Now we come along to install the type of transfer switch shown above....like the Genrac unit.
We find we only want to power one side of the multiwire branch circuit on generator so we only 're-route' one side of the circuit through the transfer switch factory supplied harness.
Is that correct?
If so that is a direct violation of 210.4(A) and it has nothing to do with the neutral.
It has to do with the circuit being capable of being supplied from two separate sources and that will happen each time the utility power comes back on while the generator is running.
Let me as you this.
With one side on utility power and the other side on generator power what would the voltage been between these two legs?
Now to make sure we are talking about the same thing.
We are talking about an existing MWBC in an existing panel.
Now we come along to install the type of transfer switch shown above....like the Genrac unit.
We find we only want to power one side of the multiwire branch circuit on generator so we only 're-route' one side of the circuit through the transfer switch factory supplied harness.
Is that correct?
If so that is a direct violation of 210.4(A) and it has nothing to do with the neutral.
It has to do with the circuit being capable of being supplied from two separate sources and that will happen each time the utility power comes back on while the generator is running.
Let me as you this.
With one side on utility power and the other side on generator power what would the voltage been between these two legs?