Situation: (2) 200 amp & (1) 150 amp main breaker panels installed inside building (grouped together). (1) 600A Meter Can mounted outside (no disconnects).
Would like to install 200A transfer switch with internal disconnect outside by meter and intercept one of the conduits going from one of the 200 amp interior panels to the exterior meter can (this is run in the concrete slab).
We only want to backup one of the 200A panels (not the other two).
Now my concern with this is the requirement to group the disconnects in 230.72. Then when I look at 230.72(B) Add'l Service Disco Means: "the additional service disconnecting means for...optional standby services permitted by 230.2 shall be installed remote from the one to six service disconnecting means for normal service"
Thoughts?
Would like to install 200A transfer switch with internal disconnect outside by meter and intercept one of the conduits going from one of the 200 amp interior panels to the exterior meter can (this is run in the concrete slab).
We only want to backup one of the 200A panels (not the other two).
Now my concern with this is the requirement to group the disconnects in 230.72. Then when I look at 230.72(B) Add'l Service Disco Means: "the additional service disconnecting means for...optional standby services permitted by 230.2 shall be installed remote from the one to six service disconnecting means for normal service"