xguard
Senior Member
- Location
- Baton Rouge, LA
We have a 480 Volt 3 phase generator with a 225 A breaker. From there we go to an automatic transfer switch with 4/0 conductors. From the transfer switch we have 2/0 conductors to a panel inside a building where they land in a distribution panel with a 175 A main breaker. The service conductors to the transfer switch from the utility are 2/0.
I don't believe the 2/0 conductors from the transfer switch to the panel inside the building are adequately protected when we are on generator power.
The run is greater than 25 feet, it also does not run take the most direct route to the panel. I'm being told the 2/0 conductors are protected by the 175A Main breaker in the dirstribution panel, I don't agree with this as they don't fall under tap rules, or service entrance conductors rules. The transfer switch is service entrance rated.
What am I missing?
I don't believe the 2/0 conductors from the transfer switch to the panel inside the building are adequately protected when we are on generator power.
The run is greater than 25 feet, it also does not run take the most direct route to the panel. I'm being told the 2/0 conductors are protected by the 175A Main breaker in the dirstribution panel, I don't agree with this as they don't fall under tap rules, or service entrance conductors rules. The transfer switch is service entrance rated.
What am I missing?