If the ATS board needs to see or use 12VDC, where would that come from using a portable generator?
Years ago I installed a Generac Genny with an ATS and if you didn't have 12 volts where you were supposed to, the ATS would not work even with the generator running.
That's in addition to the possibility of the portable genny not putting out full voltage with no load.
I wish I could see the label better. The diagram may show where the 12 volt conductors are supposed to be connected, if needed.
Ok that may be. I do very little residential ATS work but the GE-Zenith models (ZTX) step down and rectify the emergency line voltage on the motherboard to power the board and transfer the switch. The gen battery 12VDC is there just for starting the gen.