Well, let’s think about this…
A generac 26 kW has a 125A output breaker.
Doesn’t make much sense to put this generator on this house since he said the house had a 100A main.
Now sizing the generator the same as the house breaker would be a 24kW or a 22kW. These come with a 100A output breaker.
Saving some money and getting smaller, a 20kW has a 90A output breaker, and they keep getting smaller from there.
Still, you have a generator output breaker feeding the load. So if it’s a 60A, that could feed a 200A in the house panel..
the generator output will not go through the 200A OCPD on the ATS, so all is well with the generator end. Even if it did, so what..
the utility side coming from the Meterbase to the main in the panel never had any protection at all, and is probably a #2 AL going to the topside of the main breaker.
So we add an ATS for a generator, with a 200A OCPD where there NEVER WAS ONE BEFORE.
Use the #2 from the Meterbase that was going to the main, reroute it to the topside of the 200A in the ATS. Feed #2 out back to the panel main like it has been for many years.
Whats the harm?
Even with the #2 after the 200A in the ATS, it’s still better than it used to be.
And if the ATS happens to be after the main, we’ll then the size of the ATS breaker is a moot point.
In my opinion…