angel at doral
Member
Can a service entrance rated transfer switch which has no overcurrent protection be installed directly after the meter can?
Just a question to your reply, if the main panel with the ocpd is located next to the transfer switch would the main panel have to be treated as a sub panel with seperation of the egc and the grounded conductor.don_resqcapt19 said:Yes, provided the service OCPD is installed immediately adjacent thereto. 230.91
Don
wireman3736 said:if the main panel with the ocpd is located next to the transfer switch would the main panel have to be treated as a sub panel with seperation of the egc and the grounded conductor.