an 100KVA 600volt step down to 120/240 Transformer has 400amp output. We installed an 400amp Splitter as usual with 2 200amp panels out of it, but an Electrician asked why didn't we just put the 2 200amp Panels with Main shutoffs direct out of the Transformer... On an expansion and maintenance standpoint it makes sense to me, but is it permitted to install two 200amp Panels directly out of the Transformer, or is that making it an junction box?
 

Smart $

Esteemed Member
Location
Ohio
In fact, the 400A splitter route may be a violation. See 240.21(C).

Exactly what is this splitter you refer to?
 

Sahib

Senior Member
Location
India
I think without splitter, there would be more than one cable at each transformer terminal and unless the latter is rated for such termination, it may be a violation.
 

Smart $

Esteemed Member
Location
Ohio
I think without splitter, there would be more than one cable at each transformer terminal and unless the latter is rated for such termination, it may be a violation.
Under the NEC, for the most part, transformer secondary conductors must land on a single OCPD. We can split it after the OCPD. Many here describe splitting a secondary conductor as tapping a tap, which is disallowed.
 

Sahib

Senior Member
Location
India
Under the NEC, for the most part, transformer secondary conductors must land on a single OCPD. We can split it after the OCPD. Many here describe splitting a secondary conductor as tapping a tap, which is disallowed.
Is it not the 10ft tap rule allowing many sets of conductors tapped off from secondary of a transformer with primary side protection only?
 

Smart $

Esteemed Member
Location
Ohio
Is it not the 10ft tap rule allowing many sets of conductors tapped off from secondary of a transformer with primary side protection only?
No, it is not. Primary side only protection is permitted in the same section [240.21(C)], but only where you have no neutral on the secondary, e.g. a 3Ø three-wire delta output, no center tap; 1Ø two-wire output. 240.21(C) does not limit the number of secondary conductors... but each set or parallel sets must terminate in a single OCPD.
 

Sahib

Senior Member
Location
India
Smart$: The NEC handbook I have clearly shows it applies to transformer with star connected secondary also. OP is correct......
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Smart$: The NEC handbook I have clearly shows it applies to transformer with star connected secondary also. OP is correct......

Primary side only protection is not allowed with star secondary.

Smart$ already confirmed you can come off the transformer secondary lugs to more than one panel, each set has to end it's own overcurrent device.
 

Sahib

Senior Member
Location
India
Primary side only protection is not allowed with star secondary.

I think there is a misunderstanding. By 'Primary side only protection', I meant there is no OCPD immediately after the transformer star secondary but there is one OCPD at load end of each set of secondary conductors.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I think there is a misunderstanding. By 'Primary side only protection', I meant there is no OCPD immediately after the transformer star secondary but there is one OCPD at load end of each set of secondary conductors.

What would you call it where there is only overcurrent protection on the primary conductors and none on the secondary?
 

Sahib

Senior Member
Location
India
Summarizing,

Either a 400amp Splitter (or power distribution block) may be installed at the transformer secondary (with primary side protection) with 2 200amp panels out of it, provided each panel has main OCPD or the two 200amp Panels directly out of the Transformer, provided the transformer terminals are rated for more than one cable termination.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Summarizing,

Either a 400amp Splitter (or power distribution block) may be installed at the transformer secondary (with primary side protection) with 2 200amp panels out of it, provided each panel has main OCPD

This is not NEC compliant.


or the two 200amp Panels directly out of the Transformer, provided the transformer terminals are rated for more than one cable termination.

This is NEC compliant, provided each panel has main OCPD.
 