Aside from the voltage issue, having a 480V delta system presents a new set of potential problems as well; it needs to be corner gounded OR if left ungrounded, you have to add a ground fault monitoring system, all breakers and any other components must be rated for straight 480V, not "slash rated" as 480/277, anything with VFDs may not be capable of being connected and/or may not survive if they are.
If you need 480V and you have 240V, go hire a licensed electrician and have them buy you the correct transformer: 240V Delta to 480Y277, with factory documentation indicating that it is suitable for step-up. Skimping and trying to cobble together something from scrap parts will get everyone in trouble.