So I calculated load on a circuit for a new air handler was within the 45kva of my transformer.
Close but it calculated out.
I put on my fluke amp logger on after I wired it up. Wanted to verify it.
I am 5 amps over on peak for one phase.
Average amp load is 25 amps. But that really does not matter.
Hvac installer pulled out 5kw of the heat strip. After I pulled off the logger and saw that
Doing a favor for the hvac installer, ended up backfiring on me.
Trans are sensitive to heat. Room is kept cool. But I don’t know how to justify for inspector that the reduction in heat will help transformer operate higher for short periods
Close but it calculated out.
I put on my fluke amp logger on after I wired it up. Wanted to verify it.
I am 5 amps over on peak for one phase.
Average amp load is 25 amps. But that really does not matter.
Hvac installer pulled out 5kw of the heat strip. After I pulled off the logger and saw that
Doing a favor for the hvac installer, ended up backfiring on me.
Trans are sensitive to heat. Room is kept cool. But I don’t know how to justify for inspector that the reduction in heat will help transformer operate higher for short periods