don_resqcapt19 said:The code does not require that the transformer secondary have a disconnect, but Article 240 will require, in most cases, that the secondary conductors have overcurrent protection. 240.24(A) requires that this overcurrent protection be at a readily accessible location and not more than 6'7" above the floor.
dcspector said:David I disagree. The secondary ocpd does not supply the equipment per 240.24(A)(4)
dcspector said:David I disagree. The secondary ocpd does not supply the equipment per 240.24(A)(4)
raider1 said:Agreed, The overcurrent device on the secondary of the transformer is not what 240.24(A)(4) is dealing with. 240.24(A)(4) permits an overcurrent device, say for a motor, to be located above 6'7" if it is located adjacent to the utilization equipment.
Chris
iwire said:I agree not allowed by code (the disconnect location) but commonly done non the less.
Ragin Cajun said:If the transformer is feeding a nearby panelboard, a main breaker in the panel will provide secondary OC protection.
Above the ceiling is a good place to get the transformer out of the way.
RC
dnem said:240.24(A)(4) is not restricted to motors or to any other category of load.
dnem said:I know that 240.24(A)(4) uses the words "equipment" and "supply" .
dnem said:240.24(A)(4) is not restricted to motors or to any other category of load.