Transformer and Delta To Delta fed with wye

Merry Christmas

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
At the factory I work at we have a 480Y feed from utility. We run many 1980/1990s DC drives and I believe these transformers may be for isolation. Original Engineers are no longer with us.

Questions does a delta/delta transformer have a problem being fed from a wye?

If it is ok to feed delta/delta with a wye would the output of transformer act as a delta?
I assume yes?

There is a small dash symbol by H1 and X1 what does that indicate?

Thank you for your help and patience
 

Attachments

  • IMG_7786.jpeg
    IMG_7786.jpeg
    108.3 KB · Views: 25

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
At the factory I work at we have a 480Y feed from utility. We run many 1980/1990s DC drives and I believe these transformers may be for isolation. Original Engineers are no longer with us.

Questions does a delta/delta transformer have a problem being fed from a wye?

If it is ok to feed delta/delta with a wye would the output of transformer act as a delta?
I assume yes?

There is a small dash symbol by H1 and X1 what does that indicate?

Thank you for your help and patience
Yes, you can feed the delta primary of a step down transformer with the three current carrying conductors from a wye service. The secondary of the step down can either be delta or wye depending on the transformer; in your case (delta -delta) the secondary would be ungrounded delta.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The Delta primary is just the way that the transformer is internally wired. You can fed it with 480 volts and three conductors from either a Delta or a Wye system.
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Yes, you can feed the delta primary of a step down transformer with the three current carrying conductors from a wye service. The secondary of the step down can either be delta or wye depending on the transformer; in your case (delta -delta) the secondary would be ungrounded delta.
Thank you trying to figure out why some choices were made
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
The Delta primary is just the way that the transformer is internally wired. You can fed it with 480 volts and three conductors from either a Delta or a Wye system.
Thank you
 

dm9289

Industrial Maintenance Electrician
Location
Pennsylvania
Occupation
Industrial process repair/ maintenance Electrician
Yes, you can feed the delta primary of a step down transformer with the three current carrying conductors from a wye service. The secondary of the step down can either be delta or wye depending on the transformer; in your case (delta -delta) the secondary would be ungrounded delta.
Ours is just 480 to 480 no step down so that’s why I assumed it was for isolation or changing to ungrounded delta to reduce trips
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
The dash represents the relationship between the windings.
Angular displacement between the windings.
Those show no displacement between the windings

Aka Dd0
 
Last edited:

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Would that be similar to phasing dots or am I way off

Thats dot convention. It indicates the polarity of the windings. One lead in each winding is marked with a dot. When current flows into the dot in the primary, the induced currents flow out of the dots in the secondaries.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
The dash represents the relationship between the windings.
Angular displacement between the windings.
Those show no displacement between the windings

Aka Dd0
Correct.
Confusion comes with Wye windings, where the dashed line comes from the common point. Most people never see a de!ta-delta so they think the dashed lines represent the ground connection point.
 