Hello, I would very much appreciate some help in looking over my design.
I wish to install a 200 amp 3 phase, 4 wire 240/120 volt panel for small machine shop loads.
This panel will be fed through a transformer powered from an existing 3 phase 480V service.
Three phase 230 Volt 30 amp MOCP is largest motorized device (saw) that will be connected to new panel, remainder of panel capacity is for future use at this time.
Here is my plan:
Set new fused disco rated 600V with RK1 150A fuses and connect to 480V service conductors in trough per below (connection is on load side of a 400A fused service disconnect)
Feed xformer primary with 4/0 XHHW less than 25 feet, in conduit.
240.21(2) Math: 400A/0.33 = 132A minimum conductor size
Xformer primary math: FLA= 270A, PV480, SV240, so 270/(480/240) = 135A primary full load Amps
Both above good with 4/0 XHHW feeders
Install dry type 112.5KVA 480-240/120 Volt Delta standard duty transformer on floor (Transformer is oversized for safety, motor starting and minor nonlinear loads. Secondary FLA = 270 Amps)
Secondary taps will be less then 25 feet, terminate in a 200A main breaker and be 250KCM XHHW in conduit.
240.21(6) Math: Prime to secondary voltage ratio = 480/240 = 2 so 2*(0.33*150) = 99A minimum conductor size. 250KCM XHHW is good
Bonding for over 250 Volts as needed per 250.97
Bond grounded conductor in xformer and no bond connection in panel 250.30(1)
#4 CU Electrode conductor to building steel
#2 XHHW grounding conductor to disco and panel
I figure AIC at the new transformer fed panel main breaker -
Math: Transformer Z=4% and secondary FLA=270 (100/Z*I) so 100/4*270 = 6,750A minimum AIC rating required for the main Is this correct?
For above AIC, I assume infinite capacity on the primary and no impedance for the secondary conductors. Lastly on this question, I have assumed the Z at 4% because in all my looking I cannot find the exact part number my supplier has quoted me so I have gone below the lowest I could find for a 1K-factor unit rated at 112.5KVA per the supplier PDF spec sheet.
My first question is did I miss anything?
My second question is did I get the primary and secondary feeder tap requirements correct?
My third question is: Is a 10K AIC rated panel sufficient?
Thank you!
I wish to install a 200 amp 3 phase, 4 wire 240/120 volt panel for small machine shop loads.
This panel will be fed through a transformer powered from an existing 3 phase 480V service.
Three phase 230 Volt 30 amp MOCP is largest motorized device (saw) that will be connected to new panel, remainder of panel capacity is for future use at this time.
Here is my plan:
Set new fused disco rated 600V with RK1 150A fuses and connect to 480V service conductors in trough per below (connection is on load side of a 400A fused service disconnect)
Feed xformer primary with 4/0 XHHW less than 25 feet, in conduit.
240.21(2) Math: 400A/0.33 = 132A minimum conductor size
Xformer primary math: FLA= 270A, PV480, SV240, so 270/(480/240) = 135A primary full load Amps
Both above good with 4/0 XHHW feeders
Install dry type 112.5KVA 480-240/120 Volt Delta standard duty transformer on floor (Transformer is oversized for safety, motor starting and minor nonlinear loads. Secondary FLA = 270 Amps)
Secondary taps will be less then 25 feet, terminate in a 200A main breaker and be 250KCM XHHW in conduit.
240.21(6) Math: Prime to secondary voltage ratio = 480/240 = 2 so 2*(0.33*150) = 99A minimum conductor size. 250KCM XHHW is good
Bonding for over 250 Volts as needed per 250.97
Bond grounded conductor in xformer and no bond connection in panel 250.30(1)
#4 CU Electrode conductor to building steel
#2 XHHW grounding conductor to disco and panel
I figure AIC at the new transformer fed panel main breaker -
Math: Transformer Z=4% and secondary FLA=270 (100/Z*I) so 100/4*270 = 6,750A minimum AIC rating required for the main Is this correct?
For above AIC, I assume infinite capacity on the primary and no impedance for the secondary conductors. Lastly on this question, I have assumed the Z at 4% because in all my looking I cannot find the exact part number my supplier has quoted me so I have gone below the lowest I could find for a 1K-factor unit rated at 112.5KVA per the supplier PDF spec sheet.
My first question is did I miss anything?
My second question is did I get the primary and secondary feeder tap requirements correct?
My third question is: Is a 10K AIC rated panel sufficient?