High fault currents may cause the protective device to operate as fast as possible so "t" is very small, even into sub-cycle time. Low fault current may cause the protective device in its short time region so "t" might be measured in seconds.Can you briefly mention the math behind that?
My experience has been the majority locations with AFIE over 25 cal/cm*2 is due to long fault clearing times and not high available fault currents.