We recently delivered a machine that requires 240V, 3 phase to a customer who's service is 208/3 phase. They had an electrician install a 240/208 delta/wye transformer, using it in reverse as a buck boost. Shortly after the power was applied to the system, the incoming conduit started to get warm. The electrician was called in and when the transformer was opened, I noticed a ground feed was wired to X0 and another ground wire from X0 to our machine ground. No neutral was run from the main service to the transformer. At first the electrician said X0 must be bonded to ground, but later proceeded to remove both grounds from X0 and tied them together, leaving X0 floating. This appeared to solve the problem.
I deal with low voltage control circuits and was looking for input in regards to this situation.