Transformer bonding

Status
Not open for further replies.
Location
Ohio
I will be installing a 408/277 transformer for a new 208/120 panel ina retail space inside a shopping center. The MPD which it will be fed from is in another part of the building. My question is I obviously have to install a disconnect on the primary side of this installation using phase wires and a ground. The building has no copper or building steel within site or any that I have seen within any of the retail spaces to ground the secondary side of the transformer. How would you guys go about achieving this ?

Thanks in advance
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The building must have a GES (grounding electrode system) where is that located?

Welcome to the Forum. :)
 
Location
Ohio
Thanks for the reply and welcome. I have not seen MDP side system as of yet, so I'm not sure. In all of my years this will be the first time I have installed a transformer outside of the panel room and without building steel. So it did stump me. I am meeting with the building owners representative to gain access to the mechanical room next week.


Thanks again
 
Location
Ohio
Thanks again for replies. This is easier than I thought, they installed a ground plate on the same wall in the room adjacent to my equipment room it os literally 6' on other side . Everything is bonded there.
 
Location
Ohio
No, the ceiling is concrete . It's all good, the MDP on the other side of the wall along with the CT cabinet. The EGE is 6' from where my transformer will set it is a busbar mounted to the block wall everything is bonded at this point . One 1/2" hole in the wall,fire caulk and a lug then it's a done deal.
 