I was looking at a transformer and the overcurrent devices doesnt appear right.Correct me if im wrong.
Its a 75 kva 3 phase 480 primary , 120/208 secondary transformer.
the breaker feeding the transformer is 125 amps. this sounds right but the secondary breaker is 400 amps. This sounds wrong.
primary protection
75,000/(480 X 1.73)= 90 amps
90 X 1.25 = 112.5 amps
next higher size breaker is 125 amps NEC 2008 240.6(A)
secondary protection
75,000/(208 X 1.73)=208.42
208.42 X 1.25=260.52 AMPS next size up is 300 amps NOT 400 amps.
This is only for the protection of the transformer and not the conductors, but doesnt the secondary sound wrong?? am I missing something from table 450.3(B) ??