Transformer Calculations

Status
Not open for further replies.

Gary11734

Senior Member
Location
Florida
The customer has purchased a 112.5kva transformer. We have 200 amps 3phase 240v available on the primary and we want to feed a 100 amp 480v 3 phase secondary panel. It seems to me the 112.5kva is a little large for the 200 amp circuit breaker. I am rusty on calculations. Will this set up work? :?


Here's a question?

If the owner could only buy a 225 KVA transformer for this application, could you use the ampacity size you have in the question and still meet code?
 
Okay this thread might be getting a little old or redundant but when you say you have three phase 240 volt on your primary and you want to feed a 3-phase 480 volt load how do you obtain that or am I missing some information

Sent from my LGMP260 using Tapatalk
 

kwired

Electron manager
Location
NE Nebraska
Okay this thread might be getting a little old or redundant but when you say you have three phase 240 volt on your primary and you want to feed a 3-phase 480 volt load how do you obtain that or am I missing some information

Sent from my LGMP260 using Tapatalk
Um, with the transformer that the discussion is mostly about?
 

laketime

Senior Member
So customer just sent me a link saying they bought a transformer, without talking to me, that has a primary of 480v 3 phase and secondary of 208v 3 phase. Can I feel that secondary side with 240v 3 phase and still get 480v on the primary side, keep in mind feeding this backwards. Doesnt seem to me it would work but I am not good in this area.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
181228-1449 EST

Quite obviously not.

240 V on a 208 winding will severely saturate the core. And that most likely is not the only problem.

.
 