The customer has purchased a 112.5kva transformer. We have 200 amps 3phase 240v available on the primary and we want to feed a 100 amp 480v 3 phase secondary panel. It seems to me the 112.5kva is a little large for the 200 amp circuit breaker. I am rusty on calculations. Will this set up work? :?
Here's a question?
If the owner could only buy a 225 KVA transformer for this application, could you use the ampacity size you have in the question and still meet code?