Gmk said:I am looking for the best fomula to convert Megawatts into Kva. I am looking at a 7.5MW Transformer,12.4KV Primary, and 4160 secondary, and have been asked to convert to Kva.
Thanks,
GMK
Gmk said:I can nw calculate my amperage. KWx1000/Ex1.73x.8
then I can calculate my KVA by the calculation IxEx1.73/1000, is this correct am I on the right track, or is there a better way?
Thanks for the help.
GMK
Snorks said:The only way to correctly size a transformer is via the kVA values of the devices, not guessing at a PF value. And, you must also take into accout any motors that start more than twice an hour, the ambient temperature and altitude. This is assuming that your circuit harmonics are fairly normal and a K factor rated transformer is not required.