LibertyEngineering
- Allentown, PA
45kVA 480V Delta/ 120/208V Wye transfomer
Using a 70A-3P circuit breaker to feed the primary side
Feeding a 120/208Vpanel with 175A-3P main circuit breaker.
Is the 175A-3P main breaker in the panel the OCP for the conductors required per 240.21? Assuming I would not comply with 240.21 (C)(1) thru (C) (6) which would eliminate the need all together.
NEC says protection is required at the point where the conductors receive their supply. To me that means for OCP of the conductors the OCP device should be located right at the transfomer first than feed the panel.