I have a 50 KVA single phase transformer (480V primary 240V secondary) that I will use to feed a 200A Main Breaker 240V/120V panel.
I want to run (2) #3 THHN copper feeders 275' on a 100A breaker.
Can I use 80A to calculate Primary conductor size, OCPD, and voltage drop instead of the 104A rating of the transformer.
The 80A is 80% of the panel rating and allows for future expansion.
I did a 30-day demand recording. Highest recording was only 45A.
I want to keep the cost down and if I size everything @ 104A it doubles the cost e.g.... larger wire, larger disconncet and breaker jumps up to next frame size.
Thanks
I want to run (2) #3 THHN copper feeders 275' on a 100A breaker.
Can I use 80A to calculate Primary conductor size, OCPD, and voltage drop instead of the 104A rating of the transformer.
The 80A is 80% of the panel rating and allows for future expansion.
I did a 30-day demand recording. Highest recording was only 45A.
I want to keep the cost down and if I size everything @ 104A it doubles the cost e.g.... larger wire, larger disconncet and breaker jumps up to next frame size.
Thanks