I am familar with the requirements of 450 and 240 when it comes to primary and secondary conductors of a transformer, but do the requirements of 215.2(A)1 apply as well? I.E. - 75kva transformer - primary side conductor - would require a mininum of a #2 copper (115a) or larger depending on the primary OCPD - but is it permitted to be smaller? (based on the primary OCPD size) and what about the secondary conductors? - do they have to be at least 260 amps - or just large enough to meet the secondary OCPD size. (I know they cannot be smaller than the OCPD - But is a 3/0 copper permitted with a 200 amp OCPD on the secondary of this 75kva transformer? (I have concerns for the conductor between the transformer and the OCPD on the secondary side..)Thanks for the help!!