Installed a 9 kva 480/240 delta/delta trans today, for a machine. In addition to h1,2,3 and x1,2,3 there is and unlabeled conducter. What is it for. Machine needs no neutral. Should it be bonded to grd and frame?
Need more information.Installed a 9 kva 480/240 delta/delta trans today, for a machine. In addition to h1,2,3 and x1,2,3 there is and unlabeled conducter. What is it for. Machine needs no neutral. Should it be bonded to grd and frame?
Need more information.
Do you have a part number for the transformer?
What does the wiring diagram, on the nameplate, show?
Some companies (i.e. Acme) provided shielded transformers as standard, so this could be a shield connection.
If it's H-0, let it float.
If it's X-0, you can ground it, ground a phase, or install ground-detection circuitry.
Its a shield, You have an isolation transformer. The shield keeps noise from going from one winding to the other.
I'd check the voltage to ground first, just to be sure, before installing a jumper, which should be done deenergized.So should the shield conductor be bonded to the frame and EGC.
What if there is an XO?The shield gets grounded.
For sure if the transformer is Delta-Delta there is no X-0 or H-0 terminals.
Your transformer label should show if the lead is connected to a winding or a shiled. If not, as others have suggested, a check with a meter should tell you.
If it's a shield ground it.
If it is a tap to the secondary winding and not used you might cap it. If it is used then the application falls under 250.20(B).
If the secondary is delta 3 wire only then note that 250.21(B) applies and I would think if you chose to ignore a tap the same would apply.
Transformer label had a line between the winding to a grd symbol.
I am curious, why did you question the nameplate drawing?
But, grounding the shield of a transformer is definitely optional, except when you need to reduce noise that may be coupled across the transformer.
I am curious, why did you question the nameplate drawing?
But, grounding the shield of a transformer is definitely optional, except when you need to reduce noise that may be coupled across the transformer.