dparkersaltriver
Member
- Location
- LENOX
- Occupation
- contractor
I floated xo/ho and have 400v phase to phase 230 v phase to xo and 230v phase to ground
I floated xo/ho and have 400v phase to phase 230 v phase to xo and 230v phase to ground
I floated xo/ho and have 400v phase to phase 230 v phase to xo and 230v phase to ground
That suggests that your supply is a 480/277V wye, but this is not the only possibility.
Based on the nameplate, I found the following:
Do I need to connect the neutral and ground my HPS three-phase autotransformer?
$namewww.hammondpowersolutions.com
You need to bring a neutral from your source to this transformer to supply the loads.
-Jon
This machine uses a small amount of line to neutral but some of the small motors are var drive single phase which uses the neutral . ill have to get a 15 kva 480 delta to 400 wye transformer
No can do new machine they got the transformer with it on there specs
Thanks for the helpI don't want to see them have problems. Down the road