Hello everyone.
Our drawings show a 225kva, 3 phase transformer 480 pri. / 240, 3 phase Delta sec. feeding a 600A, 240V, 3 phase panel. The contractor is having an issue getting a 240V rated 3 phase panel. He wants to take (3) three 240V single phase panels with MCB and hook them up to the transformer with one panel on A and B, one on B and C, and one on A and C.
In theory this will work. But in section 240.21 (2) and (3) under the tap rules, it states that the secondary conductors shall terminate to a single OCPD. Which means to me that we can provide a 600A fused disconnect to a trough and tap within the trough for the three panels, which meets code. I have been in the trade for 45 years and have never seen anyone take 3 single phase panel feeders to a three-phase transformer.
With that said, does the code allow us to take three sets of single-phase conductors and tap two legs for each panel?
Our drawings show a 225kva, 3 phase transformer 480 pri. / 240, 3 phase Delta sec. feeding a 600A, 240V, 3 phase panel. The contractor is having an issue getting a 240V rated 3 phase panel. He wants to take (3) three 240V single phase panels with MCB and hook them up to the transformer with one panel on A and B, one on B and C, and one on A and C.
In theory this will work. But in section 240.21 (2) and (3) under the tap rules, it states that the secondary conductors shall terminate to a single OCPD. Which means to me that we can provide a 600A fused disconnect to a trough and tap within the trough for the three panels, which meets code. I have been in the trade for 45 years and have never seen anyone take 3 single phase panel feeders to a three-phase transformer.
With that said, does the code allow us to take three sets of single-phase conductors and tap two legs for each panel?