I'm having trouble deciding what is the proper size feeder and what size primary fuse to use for a transformer. Here is my first question:
If I have 25 ft. taps on the secondary of the transformer, does that mean the primary feeder has to be protected at its ampacity? Even if the primary feeder is outside except at the point of termination?
Second question:
What would be the right size fuse for the primary? The full load current is 105 amps. I know article 450 lets me use a 200A fuse (or even higher). But if I reduce it to say 130A, or 150A, will the fuses hold when the transformer is powered up??
Here are some more details:
I am connecting to 4160V with a fusible disconnect on a pole. From the disconnect, I have a cable running underground in conduit to a 750KVA, 4160V to 480V, 3 phase transformer in a vault in a building.
I have two feeders coming off the secondary of the transformer. One set of 350KCM conductors feeds a 300A disconnect, and two sets of 600's feeds a 800A disconnect. Both are indoor taps limited to 25'.
Thanks in Advance:
Steve
If I have 25 ft. taps on the secondary of the transformer, does that mean the primary feeder has to be protected at its ampacity? Even if the primary feeder is outside except at the point of termination?
Second question:
What would be the right size fuse for the primary? The full load current is 105 amps. I know article 450 lets me use a 200A fuse (or even higher). But if I reduce it to say 130A, or 150A, will the fuses hold when the transformer is powered up??
Here are some more details:
I am connecting to 4160V with a fusible disconnect on a pole. From the disconnect, I have a cable running underground in conduit to a 750KVA, 4160V to 480V, 3 phase transformer in a vault in a building.
I have two feeders coming off the secondary of the transformer. One set of 350KCM conductors feeds a 300A disconnect, and two sets of 600's feeds a 800A disconnect. Both are indoor taps limited to 25'.
Thanks in Advance:
Steve