i have a emergency lighting ckt that feeds a .250kva xfmr 277 pri and 120 secondary, the existing circuit was installed in 77 and utilized a square d magnetic underload relay to limit the duration the the xfmr received input power, this was to allow a time interval for the hid fixtures to obtain full brightness in the event of a loss of power at night so the stairwell would be lit up. the 120v power supplies 3 incandescent fixtures over the stairwell, 2 story bldg.
these xfmrs were not fused and the underloadrelay coils are shot after 30 yrs, i am figuring on bypassing the old relays and fusing the secondary of the xfmrs, at .250 kva the load is obviously small, i counted 3 incandescent lamps over the stairwell , the connected load was approx 1 amp on the secondary
of the .250kva xfmr.
question: use a 2 amp fuse? to fuse the sec of xfmr
.250kva / 120 = 2.08 amps
the incandescent lamps are hard to change being over a stairwell and i can see why they used this timing relay to drop them out after about 3 to 5 minutes,
what other type of relay could i use to replace this underload relay?
the 277v is supplied to the relay via a lighting contactor , the relay powers the xfmr for the incandescent lamps.
thnaks
steve
these xfmrs were not fused and the underloadrelay coils are shot after 30 yrs, i am figuring on bypassing the old relays and fusing the secondary of the xfmrs, at .250 kva the load is obviously small, i counted 3 incandescent lamps over the stairwell , the connected load was approx 1 amp on the secondary
of the .250kva xfmr.
question: use a 2 amp fuse? to fuse the sec of xfmr
.250kva / 120 = 2.08 amps
the incandescent lamps are hard to change being over a stairwell and i can see why they used this timing relay to drop them out after about 3 to 5 minutes,
what other type of relay could i use to replace this underload relay?
the 277v is supplied to the relay via a lighting contactor , the relay powers the xfmr for the incandescent lamps.