- Location
- Hesperia, Ca
I am installing several dry type transformers in a new electrical room. We installed a buss bar in electrical room and attached it to the Shell and Core Grounding system, which is attached to Ufer and Building steel.
I brought my GEC for each transformer from my buss bar to a ground buss in the Transformer installed by factory. My G.F. says the inspector will call us on it because we did not hit the X0 first. I told him I will change it but I also remember an engineer telling me, while doing an inspection, that it is a common misconception .
Below are figures and codes out of the code book. The figure specifically shows GEC going to ground buss, then a ground going to X0.
Any thoughts on this. Is there specific wording that says you must hit the X0 first.


I brought my GEC for each transformer from my buss bar to a ground buss in the Transformer installed by factory. My G.F. says the inspector will call us on it because we did not hit the X0 first. I told him I will change it but I also remember an engineer telling me, while doing an inspection, that it is a common misconception .
Below are figures and codes out of the code book. The figure specifically shows GEC going to ground buss, then a ground going to X0.
Any thoughts on this. Is there specific wording that says you must hit the X0 first.