The NM connector would have to be listed for the type and size of conductor passing through it, not very likely.
I can't imagine an inspector failing an install over something like this. If this is what we've come to, that's sad.The NM connector would have to be listed for the type and size of conductor passing through it, not very likely.
Welcome to the forum. :smile:
NONMETALLIC-SHEATHED CABLE CONNECTORS (PXJV)
GENERAL
Connectors for use with nonmetallic-sheathed cable are also suitable for
use with multi-conductor underground feeder and branch circuit cable
where used in dry locations unless otherwise indicated on the carton.
Single Cable ? If single conductor Type UF cable is terminated with a
fitting not specifically recognized for use with single conductor cable, special care should be taken to assure it is properly secured and not subject
to change.
I don't know of any section that requires a connector on a GEC entering an enclosure.
When the GEC is bonded to the enclosure inside the enclosure itself there is no electrical or code reason to bond the GEC to the enclosure at the point where the GEC enters the enclosure. It is made electrically continuous when it is bonded to the terminal point inside the enclosure.Sorry to bump this thread but this is an important point that most electricians dont understand.
Cadpoint you are very close. The relevant article is 250.64(E). Basically, if the GEC passes through any ferrous metal, (enclosure, conduit, etc) the ferrous metal part must be "made electrically continuous". That means bonded to the GEC. (If its conduit it has to be bonded at both ends) The reason is inductance, or as you say the choking of current flow. Doesnt matter what kind of wire.
This is one of the most common code violations in the country.
Yes, and most resi load centers have a small ko for same thing. Thanks Don and Charlie!This reminds me of an IAEI meeting with either Jim Pauley (it was some time ago so I think it was Jim Pauley) or Alan Manche of Square D. This question came up and the response was, "why do you think we put the ?" KO in the bottom of a meter fitting?" It is for a #4 or smaller conductor to pass through to the ground rod. I believe the UL representative was Don Nisson who agreed. Right (I believe that the panel was right) or wrong, that was the end of the discussion from the panel.
I can't imagine an inspector failing an install over something like this. If this is what we've come to, that's sad.
When the GEC is bonded to the enclosure inside the enclosure itself there is no electrical or code reason to bond the GEC to the enclosure at the point where the GEC enters the enclosure. It is made electrically continuous when it is bonded to the terminal point inside the enclosure.
This is true, 250.64(E) essentially says that. But thats assuming that the enclosure is indeed bonded correctly for this ....... its not always. The point is that it has to be "electrically continuous" with the GEC, not something else. My thinking is that if the enclosure isnt bonded directly to the point (ground bar etc) where the GEC is connected, or bonded to the GEC itself, then its not legal. So it depends on how its done.When the GEC is bonded to the enclosure inside the enclosure itself there is no electrical or code reason to bond the GEC to the enclosure at the point where the GEC enters the enclosure
Dana,Don - I have always thought this was the case and have installed and passed inspections with this view...however.
Upon further reflection and reading 250.92(A) - "The non-current carrying metal parts of equipment indicated in 250.92(A)(1), (2), and (3) shall be effectively bonded together.
250.92(A)(3) - "Any metallic raceway or armor enclosing a grounding electrode conductor...."
Further, Exhibit 250.32 [2002 NEC Handbook....I'm at work and don't have my 2008 with me] shows an additional bonding bushing/jumper on the metal raceway at the service enclosure.
When I checked with my senior electrical inspector he concurs that the bonding jumper at the service equipment is a requirement.
I see from the section that you have cited that I am wrong about that. Service bonding methods are required for the GEC raceway connection to the enclosure are required.
And then applying part B of the same section. I now see that 250.92(A)(3) is not in the 2008 code. However a quick at the ROP and ROC does not indicate that this subsection should have been removed from the 2008 code. The proposal, 5-84, was only to remove the following words; "Bonding shall apply at each end and to all intervening raceways, boxes, and enclosures between the service equipment and the grounding electrode." and relocate them to 250.64(E). I did not find a comment on this proposal in the ROC.250.92 Services
(A) Bonding of Services The non–current-carrying metal parts of equipment indicated in 250.92(A)(1), (A)(2), and (A)(3) shall be effectively bonded together.
(1) The service raceways, cable trays, cablebus framework, auxiliary gutters, or service cable armor or sheath except as permitted in 250.84.
(2) All service enclosures containing service conductors, including meter fittings, boxes, or the like, interposed in the service raceway or armor.
(3) Any metallic raceway or armor enclosing a grounding electrode conductor as specified in 250.64(B). Bonding shall apply at each end and to all intervening raceways, boxes, and enclosures between the service equipment and the grounding electrode.
That wording was still in the draft version of the 2008 code and there is nothing in the ROC that would support its removal. Maybe just a printing error?Guess we got a bit off track from the original XO querry - I too see the removal of this code section in 2008....I wonder what happened between the ROP and the publication to remove this section??