Transformer grounding detail

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
THE DRAWING DOES NOT SHOW ONE AT THE TRANSFORMER.

Are you just assuming there's a factory installed jumper in the transformer? If that's your concern then ask the person who submitted the drawing about it. Maybe they know something about their transformer that you don't.

Attached this post: See the red line that has arrow point that has G.

Also see the red line that has arrow point N.

N is neutral and G is equipment grounding conductor primary.

You see that G is bonded to xfmr case. You see that N is bonded to xfmr case.

You see that N is connected to xfmr x0. Follow red line labeled N to see that to center of wye.

You have second N to G bond at xfmr

0f7313e56895cfe07b0d76b536c52582.jpg



Sent from my iPhone using Tapatalk
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Yes there is, and, there is an absolute ton of parallel return paths just like this everywhere you look.

You see it on almost every electrical service around where the service conductors between the utility meters, transformers etc,,, and the service disconnect are contained in a conductive conduit.

JAP>

This is not service. This is at load side of main service disconnect.


NEC 2017 Article 250.30 system bonding jumper can be Either at transformer or secondary overcurrent protection. Where it says both places?


Sent from my iPhone using Tapatalk
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
There's only one.

You literally only drew one red line that ends at XO. XO is the neutral point of the secondary.

How are you misunderstanding this?

You understand that neutral secondary current only flows back to XO, right?
 

Another C10

Electrical Contractor 1987 - present
Location
Southern Cal
Occupation
Electrician NEC 2020
personally I'd still bond the XO to the transformer chassis. that way there is a definite path to an uninterrupted earth reference. I'd say your way would work but isn't as fool proof.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
NEC 2017 Article 250.30 system bonding jumper can be Either at transformer or secondary overcurrent protection. Where it says both places?
There is only one bonding jumper that is at the panel. There is a GEC to the transformer case and one to the panel not two SBJ's.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Attached this post: See the red line that has arrow point that has G.

Also see the red line that has arrow point N.

N is neutral and G is equipment grounding conductor primary.

You see that G is bonded to xfmr case. You see that N is bonded to xfmr case.

You see that N is connected to xfmr x0. Follow red line labeled N to see that to center of wye.

You have second N to G bond at xfmr

0f7313e56895cfe07b0d76b536c52582.jpg



Sent from my iPhone using Tapatalk
All of those grounds are AFTER the neutral /XO bond.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Attached this post: See the red line that has arrow point that has G.

Also see the red line that has arrow point N.

N is neutral and G is equipment grounding conductor primary.

You see that G is bonded to xfmr case. You see that N is bonded to xfmr case.

You see that N is connected to xfmr x0. Follow red line labeled N to see that to center of wye.

You have second N to G bond at xfmr

0f7313e56895cfe07b0d76b536c52582.jpg



Sent from my iPhone using Tapatalk
That is in NO WAY a second neutral to ground connection. The only neutral to ground connection is shown at the panel. A path via a GEC or EGC does not make a neutral to ground connection.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
There's only one.

You literally only drew one red line that ends at XO. XO is the neutral point of the secondary.

How are you misunderstanding this?

You understand that neutral secondary current only flows back to XO, right?

I see. So all thats missing is supply side bonding jumper then? You cant have effective fault current path thru earth no?


Sent from my iPhone using Tapatalk
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
The GEC bonding jumper from the transformer case to the ground rod is not code required, but it is not prohibited either. My personal opinion is that it needs an EGC (or maybe a SSBJ?) between the transformer case and the panelboard.
 
Last edited:

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Would this look better to you.
Drawing Kinda crude.

No and Yes

Yes but i cant just say that remove cable from rod tomxfmr case and provide ssbj between panel and xfmr. Engineer says whats wrong with what he provided post #1. Why he should remove cable from rod to xfmr case and provide SSBJ? I just dont know

No because You dont have EGC to secondary panelboard you have SSBJ different rules sizing.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The GEC bonding jumper from the transformer case to the ground rod is not code required, but it is not prohibited either. My personal opinion is that it needs an EGC (or maybe a SSBJ?) between the transformer case and the panelboard.
The transformer is on the supply side of the OCPD in the panel, so it would be a supply side bonding jumper.
 
Status
Not open for further replies.
Top