assuming that the grounding electrode conductor connects to that terminal block, the jumper would be the main bonding jumper. If the GEC connection is at the first disconnect, then the jumper would be a supply side bonding jumper, and it would not be permitted to be white. It could be any color other than white or gray.
I'm talking about the jumper that HHSTING is talking about shown in the drawing from the grounding terminal block (where the feeder neutral conductor to the panel and all the grounding electrodes are terminated ) to the actual XO terminal of the transformer.
To me where the main conductors terminate are the main termination points and other conductors are considered jumpers.
The conductor or jumper in the diagram from the actual XO terminal of the transformer to the grounding block is serving as the neutral.
If the neutral conductor from the panel was terminated directly to the XO terminal instead of the grounding block, then, the jumper from XO to the grounding block would be a bonding jumper.
Per this drawing the panel neutral is connected to the grounding block, not the actual XO terminal of the transformer.
Its getting its connection to the XO terminal of the transformer via a jumper cable which connects the two points.
Yes it is definitely a neutral, but, seeing as how the panel feeder neutral is not connected directly to the XO terminal of the transformer, in this case, it's actually a Neutral Jumper.
Nothing more than an extension of an upper XO termination point to a lower one.