There is an electrical contractor I work for that had the following question.
He is completing an upgrade of the electrical distribution system in a 12 story high rise. They are adding transformers on every floor. He wanted to utilize the equipment ground bus that is an integral component in an existing bus duct as the grounding electrode for the X/O-Neutral-Grounded conductor for the new transformers. The bus duct equipment grounding conductor meets the size requirements for the electrode conductor and terminates on the ground bus where he would terminate the new riser grounding electrode if required.
I told him I thought this equipment ground conductor in the bus duct did not meet the intention of the NEC. The AHJ and the electrical engineer tell him different. In which case he is OK to do the installation as he wants to. From a technical standpoint I think they are correct, but what about the NEC?
He is completing an upgrade of the electrical distribution system in a 12 story high rise. They are adding transformers on every floor. He wanted to utilize the equipment ground bus that is an integral component in an existing bus duct as the grounding electrode for the X/O-Neutral-Grounded conductor for the new transformers. The bus duct equipment grounding conductor meets the size requirements for the electrode conductor and terminates on the ground bus where he would terminate the new riser grounding electrode if required.
I told him I thought this equipment ground conductor in the bus duct did not meet the intention of the NEC. The AHJ and the electrical engineer tell him different. In which case he is OK to do the installation as he wants to. From a technical standpoint I think they are correct, but what about the NEC?