091207-0822 EST
augie47:
I agree with you that 10 kVA is the view point to use. In our area whether Y or delta for residential or commercial up to maybe 100,000 sq-ft you see three single phase transformers. However, more usually they are delta secondary with one secondary center tapped for 120/240.
However, for your earlier calculation I would change to 5,000/120 = 41.7 A for maximum line current in contrast to 10,000/208 = 48.1 .
Power dissipation in a true three phase transformer would be different than three single phase transformers, and I have no idea how much this would change the maximum current.
.