Higher %Z yields higher losses and worse voltage regulation. Lower %Z can yield fault currents too high.Perhaps- but why not 10% or 12.5%? I've seen 14.5% Z specd to control fault current on a 13.8kv bus. Then again 8% Z is better then 2% Z so you might be right.
For substations, we traditionally try to limit fault current to 10 kA and this is sometimes achieved by requesting a higher impedance design. You have to consider the lowside equipment ratings and this used to be 8-10 kA or less so you would not want to expose these devices to higher fault currents. If you have higher rated equipment you can lower the impedance accordingly, at least to the transformer design limit.